You have 3 things to consider:
Actual available fault current at the breakers
Any series ratings in the existing situation
Fault incident energy at various locations.
You say that the upstream and downstream devices are rated 10 KAIC. If the actual available fault current is less than the rating of the other breakers, meaning that you have a 'fully rated system',
then the only requirement is that your new breaker exceed the available fault current.
But if the available fault current exceeds the breaker ratings, you may have a series rating situation. If this is the case then your new breaker needs to be rated for the available fault current with the existing breakers in series. 'Series rated systems' are only allowed with specific manufacturers testing.
Given your description of the upstream and downstream breakers, I suspect you have a fully rated system at the point where you are changing the breaker, but you don't say what the available fault current is.
Any change in breaker can change the incident energy. Because of the interplay between the various dynamic impedances of the breakers in series, incident energy can go up or down. This interplay is the reason that series ratings are required.
Changing the breaker probably means recalculating incident energy. If you have a fully rated system then the higher KAIC breaker is allowed but the change in breaker brand and rating probably triggers additional paperwork and label changes.
Jon