I am trying to find out what is code for replacing old 2 conductor receptacles.Do you have to pull new wire or can you hook it back to just the two wires.
 
Re: replacing old 2 conductor receptacles

You can install another 2 prong receptacle, a GFCI receptacle or 3 prong grounded receptacle if you can get a ground wire to that location.
 
Re: replacing old 2 conductor receptacles

related question, does ground wire need to return to panel to trip cb in a ground fault ,or can it be derived from another source (ie ground rod or cold water or building steel?)? thanks
 
Re: replacing old 2 conductor receptacles

If it was a 2 wire system you don't need the ground wire.Just label it no equipment ground.Will be plenty safe
Let me clear that up a bit.It must be a gfci receptacle

[ February 16, 2004, 10:05 PM: Message edited by: jimwalker ]
 
Re: replacing old 2 conductor receptacles

The fault clearing path originates from the source, in other words, the grounded and equipment grounding conductors must be common at the source. All due respect, are you an electrician or an apprentice?

Roger
 
Re: replacing old 2 conductor receptacles

When you say a derived source, do you mean you would run an EGC to a ground rod that doesn't already exist? If that is the case, no.

If the rod already exisits, you may comply with 250.130(C).

Remeber that the ground cannot be used as a fault clearing path.
 
Re: replacing old 2 conductor receptacles

Thanks,for all input.To answer question I am just an apprentice,but i am trying!
 
Re: replacing old 2 conductor receptacles

Originally posted by wesii:
Thanks,for all input.To answer question I am just an apprentice,but i am trying!
Theres no need to include the word JUST in your sentance. You are an apprentice. Good for you. Keep it up, nobody knows everything.
 
Re: replacing old 2 conductor receptacles

Wesii, you are at the right place to learn. My question was actualy for Spark1now and was asked only for clarification.

Roger
 
Re: replacing old 2 conductor receptacles

roger,
i'm an electrician who hasn't done much work in older residential (ind & comm only). i know code requires to go back to panel (or gfi w/ identification of no ground), but am curious of reason. ie breaker wouldn't trip?

another related question how about adding a isg ground bus to panel. how would you ground the new isg ground bus? should i start a new thread on this question? thanks
tom
 
Re: replacing old 2 conductor receptacles

With the GFCI recpt, the breaker back at the panel would trip on ordinary overload or L/N short. The GFCI device only trips when it detects ~5ma leakage/imbalance between L/N. In theory, if you were standing on something dry and well insulated and stuck a paper clip into the GFCI, there may not be enough to cause a trip.

I don't see a need for a seperate IG bar back at the main panel - that as far back as you'd normally go with the IG's anyway. They are allowed to "pass through" other panels along the way back to the main without connection.
 