1) They're feeder disconnects. These are fed of a main switchboard located else where on the property.1) Are those feeders or service disconnects?
2) Are these feeding dwelling units?
3) Do the the feeder terminations at their respective panelboards or loads have a MCB or local disconnecting means?
4) Are the meters customer owned or utility owned?
Aside from the possible code issues, if one tenet overloads the circuit then you will get multiple tenants without power rather than them tripping their own OCPD. You also have an odd number of sections. 3 disconnects, another 3, then 4 which means you will have 1 outlier on a 3ph circuit. Unless these are all 3ph fused disconnects.
Might want to double check something tells me they could be three pole switches but might be switching neutral with one pole? Hopefully no fuse in the neutral if that is the case.Each fused disconnect is 3Ph (according to the existing as-bults).
1) They're feeder disconnects. These are fed of a main switchboard located else where on the property.
2) They're feeding dwelling units.
3) Unsure if the downstream panels have a line side disconnect switch.
4) the meters are utility owned.
Each fused disconnect is 3Ph (according to the existing as-bults).