Replacing receptacles at assisted living residences

Status
Not open for further replies.
Do the replacements have to be TR?

Typically you're permitted to replace defective devices with like or similar devices which does not in and of itself trigger any "new work" clause. You're simply restoring to a pre-existing condition. Check with your building/electrical official. If it were up to me, I'd say "no". :smile:
 
Typically you're permitted to replace defective devices with like or similar devices which does not in and of itself trigger any "new work" clause. You're simply restoring to a pre-existing condition. Check with your building/electrical official. If it were up to me, I'd say "no". :smile:

I agree and I would say no as well.
 
Do the replacements have to be TR?
Depends on who's paying the bill. :D

If you're the maintenance guy, your paycheck is partly tied into not spending money... replace it with a regular receptacle.

If you're a contractor or an employee of a contractor, your paycheck is partly tied into selling material... replace it with a TR. You wouldn't replace an old receptacle next to a sink and not install a GFCI, would you?
 
So if you guys where to change an old bathoom receptacle you do not feel a GFCI would be? required


In my personal opinion the new receptacles are in fact new work and would have to be TR along with complying with 406.3(D).

I can see an AHJ going either way and for that reason I recommend that Hendrix either use TRs or talk with the inspector before going with regular.
 
So if you guys where to change an old bathoom receptacle you do not feel a GFCI would be? required


In my personal opinion the new receptacles are in fact new work and would have to be TR along with complying with 406.3(D).

I can see an AHJ going either way and for that reason I recommend that Hendrix either use TRs or talk with the inspector before going with regular.
I agree iwire that Hendrix should check with the AHJ. What if you had a bad 2-wire receptacle with no ground present would you install a gfic or a 3-wire and a ground wire or just replace the 2-wire receptacle with another 2-wire receptacle? Do they make a 2-wire TR?:smile:
 
What if you had a bad 2-wire receptacle with no ground present would you install a gfic or a 3-wire and a ground wire or just replace the 2-wire receptacle with another 2-wire receptacle? Do they make a 2-wire TR?:smile:

There is no question I have to comply with 406.3(D) and now if the receptacle happens to also be in a spot that requires TR IMO I have to do that as well.

So in your example I would install a TR GFCI marked "No Equipment Ground"
 
There is no question I have to comply with 406.3(D) and now if the receptacle happens to also be in a spot that requires TR IMO I have to do that as well.

So in your example I would install a TR GFCI marked "No Equipment Ground"

That would be the best way to solve the problem.:smile:
 
...............
In my personal opinion the new receptacles are in fact new work and would have to be TR along with complying with 406.3(D). .......

I'll have to agree with respect to receptacles due to a provision within our Residential Code of NYS at Appendix J ?AJ407.1 exception 1. which states: "Replacement of electrical receptacles shall comply with the applicable requirements of Chapter 38 of this code", which at 3802.1 requires GFCI-protected receptacles in bathrooms. :)

I'd have to look further to see if this occupancy (assisted living) is SFD.
 
I'd have to look further to see if this occupancy (assisted living) is SFD.[/QUOTE]

That, I think, is the major concideration. The folks that live there are older and sometimes have problems plugging into a regular receptacle.
BTW how did GFCI's enter the equasion?:confused::confused:
 