Do the replacements have to be TR?
Do the replacements have to be TR?
Typically you're permitted to replace defective devices with like or similar devices which does not in and of itself trigger any "new work" clause. You're simply restoring to a pre-existing condition. Check with your building/electrical official. If it were up to me, I'd say "no". :smile:
Depends on who's paying the bill.Do the replacements have to be TR?
I agree iwire that Hendrix should check with the AHJ. What if you had a bad 2-wire receptacle with no ground present would you install a gfic or a 3-wire and a ground wire or just replace the 2-wire receptacle with another 2-wire receptacle? Do they make a 2-wire TR?:smile:So if you guys where to change an old bathoom receptacle you do not feel a GFCI would be? required
In my personal opinion the new receptacles are in fact new work and would have to be TR along with complying with 406.3(D).
I can see an AHJ going either way and for that reason I recommend that Hendrix either use TRs or talk with the inspector before going with regular.
What if you had a bad 2-wire receptacle with no ground present would you install a gfic or a 3-wire and a ground wire or just replace the 2-wire receptacle with another 2-wire receptacle? Do they make a 2-wire TR?:smile:
There is no question I have to comply with 406.3(D) and now if the receptacle happens to also be in a spot that requires TR IMO I have to do that as well.
So in your example I would install a TR GFCI marked "No Equipment Ground"
...............
In my personal opinion the new receptacles are in fact new work and would have to be TR along with complying with 406.3(D). .......