I'm looking at a customer's industrial facility that has an extremely old electrical system. They have their own outdoor substation and receive a primary service from the utility. One of the outdoor transformers that feeds the building is a 13.2kV delta to 480V delta, with the secondary side being ungrounded. The secondary wires run into the building and land on an exposed bus arrangement in the electric room that has a number of exposed fused knife switches fed directly off of it.
We would like to replace the secondary conductors and install a new switchboard/panelboard to replace the exposed bus arrangement and knife switches. The question is, given what we are replacing, do you believe the NEC requires us to turn the 480V side into a grounded system (assuming the system doesn't meet the requirements of 250.21(A))?
We would like to replace the secondary conductors and install a new switchboard/panelboard to replace the exposed bus arrangement and knife switches. The question is, given what we are replacing, do you believe the NEC requires us to turn the 480V side into a grounded system (assuming the system doesn't meet the requirements of 250.21(A))?