I'm looking at an application that has a single 480V 450kW generator with an internal 800A breaker which feeds two MCC lineups through a tie breaker between the MCC's. The feeder cable between the generator and the first MCC is (2) sets of 500MCM.
The MCC's are being planned for replacement and it is desired to re-configure the generator feeds so that the generator feeds each of the MCC's separately without a tie between the MCC's (ATS in each MCC). The load on each of the new MCC's is less than 400A.
To accomplish this it was discussed replacing the single 800A breaker in the generator with two 400A breakers witch each of these breakers feeding each MCC through a 500MCM cable.
Are there any code issues with replacing this 800A breaker with two 400A breakers in the generator? Can you keep the existing generator leads as they are and land them on one 400A breaker and jumper over to the other, or must you re-configure the generator leads so that the leads feed each breaker separately?
The MCC's are being planned for replacement and it is desired to re-configure the generator feeds so that the generator feeds each of the MCC's separately without a tie between the MCC's (ATS in each MCC). The load on each of the new MCC's is less than 400A.
To accomplish this it was discussed replacing the single 800A breaker in the generator with two 400A breakers witch each of these breakers feeding each MCC through a 500MCM cable.
Are there any code issues with replacing this 800A breaker with two 400A breakers in the generator? Can you keep the existing generator leads as they are and land them on one 400A breaker and jumper over to the other, or must you re-configure the generator leads so that the leads feed each breaker separately?