Replacing Tie CB in MTM

Merry Christmas

anbm

Senior Member
Location
TX
Occupation
Designer
To replace the Tie breaker in MTM switchgear configuration, I assume both M1 and M2 breakers must be off?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
To replace the Tie breaker in MTM switchgear configuration, I assume both M1 and M2 breakers must be off?
Yes.
That is why I like the MTTM configuration, as it allows complete isolation of both breakers and cells
 

anbm

Senior Member
Location
TX
Occupation
Designer
Yes.
That is why I like the MTTM configuration, as it allows complete isolation of both breakers and cells
How’s about replacing M1, does M2 need to be off or only the poco transformer powers M1 off and Tie CB - M1 connection is open?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
How’s about replacing M1, does M2 need to be off or only the poco transformer powers M1 off and Tie CB - M1 connection is open?
Is this drawout switchgear?
If these are hard bussed breakers how many sections separate the main from the Tie? Do you plan to ground the bussing?
 

anbm

Senior Member
Location
TX
Occupation
Designer
Is this drawout switchgear?
If these are hard bussed breakers how many sections separate the main from the Tie? Do you plan to ground the bussing?
Yes, switchgear has all draw out breakers, M1, M2, Tie has its own section, the configuration like this: M1 section, M1-Distribution breaker section, Tie section, M2-Distribution breaker section, M2 section.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Yes, switchgear has all draw out breakers, M1, M2, Tie has its own section, the configuration like this: M1 section, M1-Distribution breaker section, Tie section, M2-Distribution breaker section, M2 section.
If the Tie breaker is removed/racked out many if not most companies consider the sections as being deenergized, except for the section containing the tie breaker and those fed by the closed main. They would allow work in your sections M1 and M1-Distribution.
 