Yes, don't forget the labels that only mean something to electriciansRemember labeling requirements. 406.4(D)(2)
Thats right, inspectors can Red Tag if GFCI testers wont trip the device.What are they planning to plug into those receptacles? See 250.114
The "right" way to use a plug-in GFCI tester with non-grounding or non-grounded receptacles would be to plug it into a grounding cheater with the green tab or wire extended and clipped onto a known ground.Thats right, inspectors can Red Tag if GFCI testers wont trip the device.