Existing 200a MSP has 60a breaker and 6AWG copper supplying a 5-ton HVAC with outside service disconnect pull-fuse.
I want to remove the disconnect box, replace with a 100a subpanel, and install 2 breakers inside: 60a breaker for HVAC (I’ll merely relocate the service disconnect box) and a new 40a PV breaker.
Does anyone see problems here?
By my reasoning: The 40a PV fits within the original 200a per the 125% rule at the MSP.
Meanwhile, within the new subpanel, the HVAC (draw from grid) and PV (supply to grid) counteract each other along that 6AWG/60a from MSP and would therefore not overwhelm.