Installer
Senior Member
- Location
- DesMoines, Washington
A contractor submitted this 25-conductor Lighting Control cable under NEC Article 727 Instrumentation Tray Cable which allows it to be used in a 120 VAC 5A application.
When I checked the Control Circuitry, I realized that it was running at 10 A.
I'm trying to recommend a suitable 120 VAC 10 A 25 Conductor Cable for use as a Control Cable.
Article 725 has always been difficult for me.
Does Article 725 now govern the Cable Selection? If so, is this a Class 1 Cable?
Could anyone help state what specifications in 725 apply? Or even recommend a suitable cable ?
Thank you in Advance
Installer

When I checked the Control Circuitry, I realized that it was running at 10 A.
I'm trying to recommend a suitable 120 VAC 10 A 25 Conductor Cable for use as a Control Cable.
Article 725 has always been difficult for me.
Does Article 725 now govern the Cable Selection? If so, is this a Class 1 Cable?
Could anyone help state what specifications in 725 apply? Or even recommend a suitable cable ?
Thank you in Advance