I have a new project on a campus that is fed by an existing Medium Voltage (MV) 12.470V/3-phase campus loop. We are putting a new high-rise building on the campus and tying to an existing MV pad mounted source switch. I ran the preliminary fault current calcs using the infinite bus method at the source. Now I need to run a more precise fault calculation. I need to ask the utility company for the available fault current. I usually ask the utility company for the available fault current and they give me this info at the primary or secondary terminals of the service transformer. In this case there is no utility transformer, the project is providing a 12470V-480Y/277V XFMR. Can I ask the utility for the available fault current at the MV pad mounted source switch? Is this standard practice? Is this info that they would typically be able to give me? Or will they need to calc this since it's not at a utility transformer?