Hi Guys,
Good day! Please help me to size my back-up generator as alternative supply for a 300 HP fire pump. What would be the kVA rating of my generator?
Loaded question because generator sizing depends on many factors including motor starting code for the fire pump and voltage dip, frequency shift and starting kva capabilities of the genset. these factors in turn depend on engine and barrel size, fuel type, generator size. all of those depend on the manufacturer. i would suggest contacting one (or more) of the major manufacturers (cummins, cat, kohler, etc) and see what they say when you tell them you are using a standby generator for fire pump service. they will likely want a data sheet of the motor you intend to use.
since we are working with a fire pipe, you must also design the power feed such that, when the motor starts, the voltage at the line side of the motor controller does not fall below 15% of the controller's rated voltage. we must take into consideration that the generator's voltage will drop in response to the motor starting and the resulting current, at the starting power factor, will have a measurable voltage drop between the genset and the controller.