R RickGV Member Jan 6, 2006 #1 Is 36" required in "ALL" directions from electrical equipment (600 volts, nominal or less) or can we have greater than 36" in front and back and only 30" horizontally on the side (i.e right or left side)?
Is 36" required in "ALL" directions from electrical equipment (600 volts, nominal or less) or can we have greater than 36" in front and back and only 30" horizontally on the side (i.e right or left side)?
celtic Senior Member Location NJ Jan 6, 2006 #2 Re: Required Clearances for service What sort of "electrical equipment" are we talking about here? 4000A switch gear 200A panel in a home Disconnects
Re: Required Clearances for service What sort of "electrical equipment" are we talking about here? 4000A switch gear 200A panel in a home Disconnects
R RickGV Member Jan 6, 2006 #3 Re: Required Clearances for service medical imaging equipment - Cat Scan.
ron Senior Member Location New York, 40.7514,-73.9925 Jan 6, 2006 #4 Re: Required Clearances for service Review Section 110.26 of the NEC. The required space depends on whether energized live parts can be exposed for servicing.
Re: Required Clearances for service Review Section 110.26 of the NEC. The required space depends on whether energized live parts can be exposed for servicing.