Required Grounding Bushings??

Status
Not open for further replies.

K1GMB

Member
Location
North Chesterfield, Virginia 23236
Occupation
Telecommunications Engineer (Master Electrician)
I am installing a new sub-panel for my Ham radio room. It is a 100 amp 240/120 Square D QO panel. I am running less than 25 feet of metallic liquid tight 1" conduit between the main electrical panel and new sub-panel. Question is regarding the need to install grounding bushings on each end of the liquid tight conduit connectors? I have searched the 2020 NEC and I cannot find anything. I thought at one time it was required for ampacity OVER 100 amps. Any thoughts on this?? Thanks
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
There is not an XXX.46 for article 350 (like 344.46), so you need to refer to 300.4.G.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I thought at one time it was required for ampacity OVER 100 amps. Any thoughts on this?? Thanks
For a feeder the condition that would require them is with concentric or eccentric KO's and a voltage over 250 volts to ground. As Tom stated you'll need a wire type EGC run with the feeder because for 100 amps the metallic raceway cannot be used as the EGC {250.118}.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
For a feeder the condition that would require them is with concentric or eccentric KO's and a voltage over 250 volts to ground. As Tom stated you'll need a wire type EGC run with the feeder because for 100 amps the metallic raceway cannot be used as the EGC {250.118}.
What is/was the reasoning for that?
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
It use to be if there are concentrics then a ground bushing is needed even with a ground wire within the same pulled circuit.

No concentrics did not require a ground bushing, point was that the connection of connector to enclosure typically is much less likely to break apart as a concentric KO could.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It use to be if there are concentrics then a ground bushing is needed even with a ground wire within the same pulled circuit.
When was that? The NEC only requires a bonding bushing around concentric or eccentric KO's when the voltage is over 250 volts to ground. Boxes listed for bonding over 250 volts would not require the bonding bushing even when the voltage is over 250 volts to ground.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
It use to be if there are concentrics then a ground bushing is needed even with a ground wire within the same pulled circuit.

No concentrics did not require a ground bushing, point was that the connection of connector to enclosure typically is much less likely to break apart as a concentric KO could.
Sorry, but you are incorrect.
 

K1GMB

Member
Location
North Chesterfield, Virginia 23236
Occupation
Telecommunications Engineer (Master Electrician)
It use to be if there are concentrics then a ground bushing is needed even with a ground wire within the same pulled circuit.

No concentrics did not require a ground bushing, point was that the connection of connector to enclosure typically is much less likely to break apart as a concentric KO could.
Interesting, I am running a #6 THHN grounding conductor within the same liquid tight. Grounding the new sub-panel to main panel grounding. Electrically, the metallic liquid tight connectors are attached "bonded" to each electrical panel with the tightening of the retaining nut. I'm sure if I ohmed it out, I would have a good electrical connection between the metallic flex within the liquid tight and system ground. But I will ground each bushing at both the main electrical panel and the sub-panel. It's probably a good idea after all to ground the metallic flex in the liquid tight to help provide some "RF" shielding of the feeder when I eventually fire up the 1 kW amateur radio amplifier. Hopefully some RF shielding of the liquid tight, and good grounding will help reduce and or prevent RF interference within the house. My only regret is that I should have probably used 1 1/4" liquid tight. While the calculated conduit fill is less than 40%, I will say that it was a challenge (#$%^&) to pull. I had it on hand from a previous project and wanted to save some bucks.........no good deed goes unpunished....................Thanks again for the feedback!!!!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Electrically, the metallic liquid tight connectors are attached "bonded" to each electrical panel with the tightening of the retaining nut. I'm sure if I ohmed it out, I would have a good electrical connection between the metallic flex within the liquid tight and system ground. But I will ground each bushing at both the main electrical panel and the sub-panel.
The NEC does not require bonding bushings for this installation. That doesn't mean that you cannot use them.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It use to be if there are concentrics then a ground bushing is needed even with a ground wire within the same pulled circuit.

No concentrics did not require a ground bushing, point was that the connection of connector to enclosure typically is much less likely to break apart as a concentric KO could.
In this area, IF bond bushings were required to provide adequate grounding (ie: concentric, etc) without a wire type ground AND a wire type EGC was used, the bushings would still be required. In this case, with the flex involved, bond bushings would not provide the required grounding and they would not be required.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Interesting to see ground bushings on many panels at the Trade Hounds website. Seems some think they are required everywhere.
I see them needlessly installed all over the place. Almost all of the sparkies that I work with have no idea when they are or are not required so they just install them everywhere.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I see them needlessly installed all over the place. Almost all of the sparkies that I work with have no idea when they are or are not required so they just install them everywhere.
I see a lot of what I call "defensive" installs. With some portions of the NEC being a bit confusing, inspectors interpretations varying lack of training, etc., a lot of shops adopt "standards" they find less expensive than re-dos. Install grounding bushings on all services and 480v systems, always insrtall (2) ground rods, use anti-short bushings on MC, use HCF cable where not required, always use deep 4" sq boxes, etc.......
 