I'm currently involved in a project where we are feeding a new 480V panel from existing 480V switchgear in an industrial setting. The new 480V panel will serve new 480V loads as well as feed a transformer that feeds a 120/208V panel that will serve new and existing loads.
For this particular instance are we required to show existing load calculations at the 480V Switchgear where we will be feeding the new loads from? Do we need to show these load calculations on the One-Line or Riser diagram where I typically see them shown? Or in this instance is it sufficient enough to show only the new loading that will be added?
If load cannot be calculated then can the switchgear be monitored for a period to determine existing loading?
For this particular instance are we required to show existing load calculations at the 480V Switchgear where we will be feeding the new loads from? Do we need to show these load calculations on the One-Line or Riser diagram where I typically see them shown? Or in this instance is it sufficient enough to show only the new loading that will be added?
If load cannot be calculated then can the switchgear be monitored for a period to determine existing loading?