Required neutral to service disconnect
Jpflex
Electrician big leagues
Victorville
Electrician commercial and residential
Nec 250.24 D says that if an ac system operating at 1000 volts or less is grounded at ANY point, the grounded conductors shall be routed with the ungrounded conductors to each service disconnecting means and connected to disconnecting means grounded conductors or bus...
If the utility servuce supplying the premises wiring is grounded the grounded conductor must be run to service equipment regardless if line to neutral loads are supplied.
In contradiction
Nec 250.184 B 6 says for a single point grounded neutral system:
A neutral conductor shall only be required if phase to neutral loads are supplied
Is this latter section a modification to the previous code, or referring to dc? Or why this contradiction?
250.184 is under the article of general grounding and bonding. Title is solidly grounded neutral systems.
Section 250.24 D is also in the same artice for grounding and bonding. The title here is grounding service supplied ac systems
Services have to be supplied with a neutral according to 250.24 D
However, these services can also be classified as a solidly grounded neutral system if no ground impedance input in grounding system and also considered as a single point grounded neutral system where the neutral is grounded at only 1 location such as at the supply side of the service.
With a neutral always being required at a service nec 250.184 B 6 no longer makes sence regardless of if line to neutral liads are served