Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
Nec 250.24 D says that if an ac system operating at 1000 volts or less is grounded at ANY point, the grounded conductors shall be routed with the ungrounded conductors to each service disconnecting means and connected to disconnecting means grounded conductors or bus...
If the utility servuce supplying the premises wiring is grounded the grounded conductor must be run to service equipment regardless if line to neutral loads are supplied.
In contradiction
Nec 250.184 B 6 says for a single point grounded neutral system:
A neutral conductor shall only be required if phase to neutral loads are supplied
Is this latter section a modification to the previous code, or referring to dc? Or why this contradiction?
If the utility servuce supplying the premises wiring is grounded the grounded conductor must be run to service equipment regardless if line to neutral loads are supplied.
In contradiction
Nec 250.184 B 6 says for a single point grounded neutral system:
A neutral conductor shall only be required if phase to neutral loads are supplied
Is this latter section a modification to the previous code, or referring to dc? Or why this contradiction?