I've been told by the inspector that I must use Myer's type hubs for my service gear. Here is what I currently have:
Basically it's a 200A 480v 3ph panel in a 3R enclosure attaced to a 3R tap box (for the contactors and time clock) and to the meter base. I was under the impression that if you made entry into a 3R enclosure below the level of termination blocks, you were not required to use a Myer's hub. I have used sealing lock rings going to the panel enclosure with PVC T/A's. The pipe is 3" PVC.
I understand that it's the authority having jurisdiction's final interpretation of the code, but I haven't been able to locate what part of the code governs this. My on site personnel didn't bother to ask what article of the NEC he was calling this from.
Any input is greatly appreciated!
Basically it's a 200A 480v 3ph panel in a 3R enclosure attaced to a 3R tap box (for the contactors and time clock) and to the meter base. I was under the impression that if you made entry into a 3R enclosure below the level of termination blocks, you were not required to use a Myer's hub. I have used sealing lock rings going to the panel enclosure with PVC T/A's. The pipe is 3" PVC.