Requirement scenario of a 64REF and earth fault backup(51G)

Merry Christmas

SS_EE

Member
Location
Thailand
Occupation
Engineer
Dear all,
Could you please let me know whether a 250kVA 0.48/15kV step-up transformer require the above protections? is there any recommendation from IEEE at which rating this protection is required?

This is a small take-off station of a 400 kWp ground mounted solar farm.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The National Electrical Code simply requires some type of monitoring of ungrounded systems or protection on solidly grounded systems, it is up to the designer to decide which functions to actually implement.

I can't remember employing a 64REF on a standard transformer as small as 250kVA.
 

SS_EE

Member
Location
Thailand
Occupation
Engineer
The National Electrical Code simply requires some type of monitoring of ungrounded systems or protection on solidly grounded systems, it is up to the designer to decide which functions to actually implement.

I can't remember employing a 64REF on a standard transformer as small as 250kVA.
Hi Jim, thanks for the reply. in this case what will be your recommendation. the star configuration is on the HV side
 