Thanks for the replies, and let me see if I can clarify things a little bit.
The sealoffs in question are coming up in an unclassified area, 30 yards away from the Class 1, Div 2 location. The question of boundary seals is met by boundary seals inside the hazardous location, within 10 feet of the boundary. The seals at the unclassified location never should have been installed, as they are too far away from the hazardous location to meet the 10' rule regardless. Some good points have been raised in the aspect of the fitting meeting the UL classification in some regards, but in my less than knowledgable, code reading mind, the purpose of conduit of any type is protection of the wire. If the seal off did is job of stopping hazardous atmospheres, but yet could be easily damage, thereby exposing conductors, that would be an issue. These sealoffs are cast iron, and I have difficulty thinking that would be the case, but after the discussions here I suppose it's worth asking that question.
I have the inspector here that turned me on to this site, and you folks have more than lived up to his claims in my mind. Thanks so much.
Oh one last thing, any thoughts with regard to marking. My understanding is that a poured seal off has red paint once poured as an indication that the seal off has been poured. What is your opinion if I don't have them poured?
Once again thanks for all the help, sorry for the delay in response.