Requirements for countertop outlets in laundry room or at wet bar?

Status
Not open for further replies.

tadavidson

Senior Member
Location
Georgia
Occupation
Electrical Contractor
Would anyone care to assist me in this quest for knowledge? Does the code specifically address the two areas; laundry "folding counter" and "wet bar" as far as required receptacles and or spacing?
 
Would anyone care to assist me in this quest for knowledge? Does the code specifically address the two areas; laundry "folding counter" and "wet bar" as far as required receptacles and or spacing?

or any such counter top other than in Kitchen.
 
210.8(A)7 Laundry, utility and wet bar sinks

Got that. If present must be protected. Do you know of any requirement to have any? I have a wet bar in a new house that I put a sw/recpt combo on the right side of the counter. Approx 5 feet. I put in a gfci recpt. then in retrospect began to be concerned I may should have added another liken to the kitchen 24" rule.
 
Got that. If present must be protected. Do you know of any requirement to have any? I have a wet bar in a new house that I put a sw/recpt combo on the right side of the counter. Approx 5 feet. I put in a gfci recpt. then in retrospect began to be concerned I may should have added another liken to the kitchen 24" rule.
There are no counter top receptacle requirements for wet bars or laundry rooms.
 
There are no counter top receptacle requirements for wet bars or laundry rooms.

Thanks ActionDave, , I haven't studied since the 05 cycle. I got to get busy. I couldn't find anything but I haven't studied since the o5 book.
 