I don't recall anything in the NEC that requires them.Is there any code or standard for the installation of the volt and amp meter please refer. Also please specified that are we need to install these measuring instruments on every panel/ distribution board or not.
UL508a requires a bonding wire if there are components on the door with voltages exceeding 30 V.I think there is a requirement for a hinged panel with devices attached to have an EGC jumper.
Interesting. Many/most of the systems I've experienced commonly have individual ammeters and one common voltmeter.Is there any code or standard for the installation of the volt and amp meter please refer. Also please specified that are we need to install these measuring instruments on every panel/ distribution board or not.
pretty common here too, although these days with new equipment you are as likely to see a digital power meter.Interesting. Many/most of the systems I've experienced commonly have individual ammeters and one common voltmeter.
I suspect most of the time the meters come with the new equipment rather than being field installed. It is insanely expensive to field install anything these days.In the US, some locations mat require a permit and inspection. If this is a UL508A control panel, there could listing issues. For me as a end user, I would have to install UL listed parts, the panel meters and CTs are often component recognized for install by a panel shop.
If this is an electrical panel, breakers and such, seems like the 2020 NEC has language on power metering.
There is a requirement for wire space limits, 70%, and splices, 40%.
The poster above is from Pakistan. The voltage there is 230V, 50 Hz. I don't know the requirements there are UL, NEC, or IEC or something else. Perhaps he can clue us in...........In the US, some locations mat require a permit and inspection. If this is a UL508A control panel, there could listing issues. For me as a end user, I would have to install UL listed parts, the panel meters and CTs are often component recognized for install by a panel shop.
If this is an electrical panel, breakers and such, seems like the 2020 NEC has language on power metering.
There is a requirement for wire space limits, 70%, and splices, 40%.
It is a main distribution panel that is consisting of different capacity breakers.I gave an answer for the NEC.
NEC requires product listing. See article 100 definition.
I am not familar with IEC.
What type of panel is this?