We have a project where we are replacing old electrical service equipment with a new service panelboard and at least two branch circuit panelboards. The existing service is a mess. Multiple wireways, multiple service disconnects, service conduits and connections added over the years to increase capacity, etc.
The new service equipment and panelboards are about 25 to 30 feet away from the existing. We have all types of circuit and feeder sizes to reroute to the new equipment; From small branch circuits to feeders up to 350 MCM. I would like some advice and comments on how physically to reroute these circuits. We are planning to use wireways and junction boxes to splice existing circuits and feeders and reroute new circuits to the new service equipment.
So, I install my wireway or junction box and I have to dismantle the existing conduit back to a point where I then extend a new piece from the end of the conduit into the wireway/junction box, run a new conduit from this junction point to the new equipment, splice on to the existing conductors and connect circuit or circuits to a new circuit breaker(s). In my first step in dismantling the conduit what would be the best way to handle the existing conductors in the raceways? I suppose we could attach a pull rope to the conductors, go the nearest pull point beyond our junction point, pull back beyond new junction point, install new raceway into the junction point, and pull conductors into the junction/splice point.
Is it acceptable or feasible at least for small conductors to dismantle the conduit with conductors in them back to the termination point, cut the conductors to proper length, and install conduit over the conductors and into the junction/splice point? I was also thinking of installing conduit bodies on the end of the conduits to extend new feeders/circuits into the junction/splice point.
I would appreciate any comments or suggestions on the best approach to rerouting and splicing of the conductors.
Thanks.
The new service equipment and panelboards are about 25 to 30 feet away from the existing. We have all types of circuit and feeder sizes to reroute to the new equipment; From small branch circuits to feeders up to 350 MCM. I would like some advice and comments on how physically to reroute these circuits. We are planning to use wireways and junction boxes to splice existing circuits and feeders and reroute new circuits to the new service equipment.
So, I install my wireway or junction box and I have to dismantle the existing conduit back to a point where I then extend a new piece from the end of the conduit into the wireway/junction box, run a new conduit from this junction point to the new equipment, splice on to the existing conductors and connect circuit or circuits to a new circuit breaker(s). In my first step in dismantling the conduit what would be the best way to handle the existing conductors in the raceways? I suppose we could attach a pull rope to the conductors, go the nearest pull point beyond our junction point, pull back beyond new junction point, install new raceway into the junction point, and pull conductors into the junction/splice point.
Is it acceptable or feasible at least for small conductors to dismantle the conduit with conductors in them back to the termination point, cut the conductors to proper length, and install conduit over the conductors and into the junction/splice point? I was also thinking of installing conduit bodies on the end of the conduits to extend new feeders/circuits into the junction/splice point.
I would appreciate any comments or suggestions on the best approach to rerouting and splicing of the conductors.
Thanks.