Can we use table Table 310.15(B)(6) and parallel conductors if the service is over 400? For instance, on a 1200 amp Res. Service can we run (3) 400MCM since one is good for a 400 amp service?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
wyboy said:
Can we use table Table 310.15(B)(6) and parallel conductors if the service is over 400? For instance, on a 1200 amp Res. Service can we run (3) 400MCM since one is good for a 400 amp service?

Welcome to the Forum. Interesting question.

The table heading says 3-wire.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
wyboy said:
Can we use table Table 310.15(B)(6) and parallel conductors if the service is over 400? For instance, on a 1200 amp Res. Service can we run (3) 400MCM since one is good for a 400 amp service?

If your service is rated 1200 amps then T310.15(B)(6) does not apply, IMO
 

peter d

Senior Member
Location
New England
wyboy said:
Can we use table Table 310.15(B)(6) and parallel conductors if the service is over 400? For instance, on a 1200 amp Res. Service can we run (3) 400MCM since one is good for a 400 amp service?

1200 amp residential service? Are you wiring a castle by any chance?
 

wirenut1980

Senior Member
Location
Plainfield, IN
I would say if you wire each set of 400 kcmil copper to three separate 400 amp breakers/panels from a single main disconnect where all conductors are terminated, you could use the table. They would not be paralleled after the main disconnect, but I think it would work.
 

480sparky

Senior Member
Location
Iowegia
wirenut1980 said:
I would say if you wire each set of 400 kcmil copper to three separate 400 amp breakers/panels from a single main disconnect where all conductors are terminated, you could use the table. They would not be paralleled after the main disconnect, but I think it would work.

Those would be branch circuits, not feeders. Then the table is out the window.
 

wirenut1980

Senior Member
Location
Plainfield, IN
480sparky said:
Those would be branch circuits, not feeders. Then the table is out the window.

I am interpreting the definitions in Article 100 for "feeder" and "branch circuit" to say that the conductors in question are feeders.
 

C3PO

Senior Member
Location
Tennessee
wirenut1980 said:
I am interpreting the definitions in Article 100 for "feeder" and "branch circuit" to say that the conductors in question are feeders.

They are feeders, but none of them would be the "main power feeder" so 310.15(B)(6) does not apply.
 

charlie

Senior Member
Location
Indianapolis
peter d said:
1200 amp residential service? Are you wiring a castle by any chance?
We permit 1? residential services up to 1600 amperes but the load is not there. The Code requires a lot of additional size if the equipment is there but one family can't use it all at the same time unless it is Thanksgiving or a large party is in progress. A lot of people may increase the load for a short period of time but not for a long enough time to overload our transformer and secondary to the point of being undersized. It seems to me that a lot of ultra-large homes have multiple services to get lots of circuits and not for the load.

C3PO said:
They are feeders, but none of them would be the "main power feeder" so 310.15(B)(6) does not apply.
I agree 100% :smile:
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
charlie said:
A lot of people may increase the load for a short period of time but not for a long enough time to overload our transformer and secondary to the point of being undersized.
What about the individual premises' service drop/lateral and entrance? They don't enjoy the utility's diversity during those times.
 

charlie

Senior Member
Location
Indianapolis
LarryFine said:
What about the individual premises' service drop/lateral and entrance? They don't enjoy the utility's diversity during those times.
The majority of the time, a home of this size will have their own transformer and the transformer secondary would be the service lateral. There is no diversity since there is only one customer; however, there is an extremely large amount of diversity in the use of power in the home. Even in the case of 10,000 to 15,000 square foot homes, a 75 kVA 1? transformer will work. We would install just two sets of 500 kcmil Al triplex service laterals to a 1,600 ampere residential service. Looking at the NEC, we are almost 1,000 amperes short of being able to serve the home but we don't have any problems. :)
 