From 2008 NEC Questions and Answers April Part 2
Based on other calculation approaches we believe there is an error in your response.
A 15A circuit breaker has been commonly used with 13 receptacles because of this misunderstanding, but even with a 20A circuit breaker, you cannot load it 100% without it being rated for that use. Most residential panels do not have such breakers. Diversification of loads does not come into play till 10,000VA. See corrections below.
Q2. How many receptacles can be installed on a general-purpose branch circuit?
A2. The NEC doesn?t limit the number of GFCI-protected receptacle outlets on a general-purpose branch circuit in a dwelling unit [220.14(J)], but for other than dwelling units, the NEC limit is 13 receptacle outlets each at 180VA per mounting strap [220.14(I).
Circuit VA = Volts x Amperes
Circuit VA = 120V x 20A (16 Ampere trip) (15A CB = 12A trip)
Circuit VA = 2,400 VA (1920) (1440)
Number of Receptacles = 2,400 VA/180 VA
Number of Receptacles = 13 (10.6) (8)
Based on other calculation approaches we believe there is an error in your response.
A 15A circuit breaker has been commonly used with 13 receptacles because of this misunderstanding, but even with a 20A circuit breaker, you cannot load it 100% without it being rated for that use. Most residential panels do not have such breakers. Diversification of loads does not come into play till 10,000VA. See corrections below.
Q2. How many receptacles can be installed on a general-purpose branch circuit?
A2. The NEC doesn?t limit the number of GFCI-protected receptacle outlets on a general-purpose branch circuit in a dwelling unit [220.14(J)], but for other than dwelling units, the NEC limit is 13 receptacle outlets each at 180VA per mounting strap [220.14(I).
Circuit VA = Volts x Amperes
Circuit VA = 120V x 20A (16 Ampere trip) (15A CB = 12A trip)
Circuit VA = 2,400 VA (1920) (1440)
Number of Receptacles = 2,400 VA/180 VA
Number of Receptacles = 13 (10.6) (8)