Does this look right to size my wire? 200 amp service single family dwelling using ser cable AL. 200 x .83 = 166. 310.15(B)(16). 60 degree column for aluminum would be 250 KCmil. If this is true why do most use 4/0, 4/0, 4/0, 2/0?
Does this look right to size my wire? 200 amp service single family dwelling using ser cable AL. 200 x .83 = 166. 310.15(B)(16). 60 degree column for aluminum would be 250 KCmil. If this is true why do most use 4/0, 4/0, 4/0, 2/0?
You have zeroed in on a controversial Code Section that has been cussed and discussed a length since Art 338.10 was modified in 2008. There was debate prior to 310.15(B)(7) being changed to the "83%" rule. Meanwhile 338.10 was modified to SE only being 60° when installed in insulation.
FWIW, I would agree with your post if the SE is insulation and taking into account 310.15(A)(2) exception.
In most installs the 75° ampacity can be used as Jumper pointed out
So the answers are:
Yes, no, maybe, possibly.
I hate 310.15