Hi,
Is it code compliant to install a 15 amp toggle/rocker switch on a 20 amp, 12-2 wire, circuit in a dwelling unit? 2020 NEC, Section 404.14, seems to require a 20 amp switch on a 20 amp circuit.
Thank You.
 
Hi,
Is it code compliant to install a 15 amp toggle/rocker switch on a 20 amp, 12-2 wire, circuit in a dwelling unit? 2020 NEC, Section 404.14, seems to require a 20 amp switch on a 20 amp circuit.
Thank You.
If the switch controls a receptacle, then it has to be rated the same as the OCPD (404.14(F)). If the switch is for a permanent connected load, like overhead lights, then as long as the connected load doesn't exceed the switch rating you could use a 15 amp switch on a 20 amp circuit (404.14(A)(1) - (3)). Answer based on 2017, don't have the 2020 yet.
 
Okay so I recently designed a workshop where the customer wanted to install a series of these new handy-dandy chain-hung LED strip lights that are daisy-chained together by all having 5' cords with 5-15P plugs and 5-15R receptacles on the opposite ends from the cord entry points of each light. So I put a receptacle in the ceiling specifically for these lights. In this case it was a 15A circuit with 14/2NM. But I had considered making it a 20A circuit. In this case I would have still installed a 15A switch since the lighting load was only going to be about 4 amps. Since it has a receptacle outlet, would that have been a violation if I had done it that way? (20A circuit, 15A switch, dedicated lighting load of 4 amps)
 
From what someone recently posted, a receptacle requires the switch be rated for the circuit, while hard-wired lighting doesn't.

A ceiling receptacle intended for stationary lighting may be questionable; in your example, I would probably use a 15a switch.
 
Thanks Larry! I think in the future, should I ever come across this situation again I'll just spec out a 20 amp switch AND receptacle just to avoid any question. It's not worth the few pennies of savings if it gets questioned by an inspector. Thanks for the reply!
 
If the switch controls a receptacle, then it has to be rated the same as the OCPD (404.14(F)). If the switch is for a permanent connected load, like overhead lights, then as long as the connected load doesn't exceed the switch rating you could use a 15 amp switch on a 20 amp circuit (404.14(A)(1) - (3)). Answer based on 2017, don't have the 2020 yet.
Never was aware of this rule and not sure how far back it goes. I do see that it is also in 2014 NEC. There is an exception in 2014 that could use a little better wording IMO but basically allows a 15 amp switch to supply an individual 15 amp receptacle that is otherwise on a 20 amp circuit.
 
Okay so I recently designed a workshop where the customer wanted to install a series of these new handy-dandy chain-hung LED strip lights that are daisy-chained together by all having 5' cords with 5-15P plugs and 5-15R receptacles on the opposite ends from the cord entry points of each light. So I put a receptacle in the ceiling specifically for these lights. In this case it was a 15A circuit with 14/2NM. But I had considered making it a 20A circuit. In this case I would have still installed a 15A switch since the lighting load was only going to be about 4 amps. Since it has a receptacle outlet, would that have been a violation if I had done it that way? (20A circuit, 15A switch, dedicated lighting load of 4 amps)

Off topic, but how did you install the required GFCI protection for those lights?
 