Residential 2 hour rated fire wall

Status
Not open for further replies.

bkelly

Member
What are the requirements or limitations for nm cable and plastic boxes in a residential 2 hour rated firewall in townhomes. From what I can understand, a 2 hour rated, load bearing wood stud wall between the townhomes, woiuld require conduit for the nm cable. Any one have any info on this?
 
dealt with that on apt building only needed puddy pads if plastic carlon boxes were in same bay as joining unit nm allowed with typical nail on carlon check with ahj
 
With the description you give, it sounds like the entire wall assembly is the fire barrier, and not just one side. That is, the fire rating is obtained by using both wall faces together.

This means rated boxes or enough 'putty pads' to get the rating, sealed penetrations, and no stud bays with penetrations on both sides.

The fire tests simply don't care if the electrical is in pipe or cables. What does matter is what the approved prints specified.

I don't see how 'load bearing' has any relevance to the wiring method either.
 
I would talk to your Structural Inspector to get the particulars about this.

In Oregon it goes kind of like this:

boxes may not exceed 16 square inches,
no more than 100 sq in of membrane penetrations in 100 sq ft of wall area,
boxes on opposite side of partition must be seperated by not less than 24"
you may use other methods per their listing, putty, tested boxes, etc.

There are boxes out there that per their listing may be placed as close as 3 1/2", if I remember correctly they were Allied and Union. You would have to get their documetation to verify this though.

This can be pretty hard to comply with when kitchens are put back to back.

Good luck~
 
should be on the plans, if not get the architect or engineer involved to cover yourself
 