The three phase motor produces effectively constant torque through each rotation, potentially reducing wear and tear on bearings and driven components. Less vibration. (That would be the more reliable part.)Do you have any literature? From what I've read, the efficiency is the same.
Plus monthly minimum charges are usually higher for three phase - more equipment/more expensive equipment for distribution to provide/maintain, energy used is usually at the same rate for either source type.Efficiency cannot be assumed, only measured (or determined from something that someone else measured). So if you look at a single phase motor that says it is 85% efficient, and a 3 phase motor that says it is 85% efficient, there is no difference. Watts are watts are watts. The delivery of MECHANICAL power to the motor is smoother for a 3 phase motor, and that will theoretically translate to longer equipment life, but if the equipment life is 25 years vs 28 years, are you going to notice?
What you might find with a 3 phase service however, is a nasty little surprise at the end of the month called a "Demand Charge" and/or a Power Factor penalty. Single phase residential services do not have these things, 3 phase usually do. So efficiency be damned, you may end up PAYING more just because you have a 3 phase service, whether or not you actually use it.
I'm not being billed based on demand. So what is the consensus here? What would you do in your house? 3-phase or 1-phase A/C?
I'd do the single phase. Try calling a service company saying you need someone to service your 3 phase residential a/c system and those people are going to fall over confused. Single phase offers off the shelf everything.
OP said three phase is already available so the why is kind of a mute point.Unless you are in an industrial/commercial area it would be highly unlikely that you would even have 3ph available at all.
Then, consider how many devices that you would have in a home that would benefit from 3ph. A 3 pH motor is extremely simple when compared to a 1ph motor but the HP that is require in a residence may make 3ph impractical.
Then, you would have to choose between a 208y/120 3ph4w and a 240d/120 3ph4w. 208v 1ph appliances are not as common as 240v.
Unless you have a very serious wood or machine shop on the premises where you may be if it from 3 pH power it is of my opinion that having a 3ph service may more for ego than practical.