dekeSC
Owner
- Location
- South Carolina
- Occupation
- Electrical Contractor
I have an estimate for a backup generator I need to put together for a 400 amp service with two 200 amp main breakers that feeds two MLO load centers that are located inside a lower level garage. Is it a typical scenario to install the ATS next to the load-center and pull the existing 4/0 AL SER cable out of the load-center and re-route it into the ATS? Or depending on the actual location of the ATS to set a junction box and intercept the 4/0 and splice a new 4/0 Al cable into the ATS? Also, the existing 400 amp service has a few branch circuit breakers installed, how would I get these on the backup generator? Or any suggestions would be greatly appreciated.