Re: Residential Breaker Sizing
What do you mean when you say you have a ?demand? of 140 amps? Is this a new (not yet built) facility, and is that figure the result of a load calculation, per article 220? If so, then you would have had to include a 125% factor as part of that calculation process, wherever it is appropriate. This would have taken care of the 80% breaker rating. So a 150 amp breaker would be acceptable.
But if this is an existing facility, and if it is undergoing a remodel project, and if the 140 amps is a measured value, then you do have to ?biggie size? the load (or equivalently, downsize the breaker rating). So a 175 amp breaker would be needed.