X xformer Senior Member Location Dallas, Tx Occupation Master Electrician Feb 4, 2014 #1 Is the requirement of 210.52(H) also included in 220.14(J)?
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Feb 4, 2014 #2 xformer said: Is the requirement of 210.52(H) also included in 220.14(J)? Click to expand... Yes, as these are just general use receptacles. No extra load has to be added to your Art. 220 calculation.
xformer said: Is the requirement of 210.52(H) also included in 220.14(J)? Click to expand... Yes, as these are just general use receptacles. No extra load has to be added to your Art. 220 calculation.