I will be Installing a single phase class 320 service for a customer of mine. 400amp Cooper Bline meter main with a 300 amp main breaker. The service will be located on a CMU wall about 150 feet from house. At the house I will be installing a 400 amp distribution panel, that will feed 2x 200 amp sub panels. My calculated load is 220 amps, hence class 320 service. He also plans on adding a 5 hp motor and 20 hp motor at a later time for for his small home machine shop equipment. My question is
1. Is it better or easier to run a set of 500mcm al in 4 inch conduit, rather than 2 parallel smaller feeds in separate conduit? I am trying to save $$ on wire, but if much better I will use cu. Trying to keep my voltage drop under 5%. Where I am at, voltage is usually about 122-124 to 244-248v. The underground section has 2x 90's and a large sweep that would equate to 90 degrees sweep.. I was a lineman many years ago so pulling wire shouldn't be that difficult.
Customer is a good friend of mine. I am just trying to be that good friend and Keep the cost down, but still give him a quality and smart installation.
We also have a 10kw pv system that will be tying into the line side of the meter main.
Your thoughts on the wire size/installation from the meter main to the 400 amp panel at the house are greatly appreciated.
Thank you.
I will be Installing a single phase class 320 service for a customer of mine. 400amp Cooper Bline meter main with a 300 amp main breaker. The service will be located on a CMU wall about 150 feet from house. At the house I will be installing a 400 amp distribution panel, that will feed 2x 200 amp sub panels. My calculated load is 220 amps, hence class 320 service. He also plans on adding a 5 hp motor and 20 hp motor at a later time for for his small home machine shop equipment. My question is
1. Is it better or easier to run a set of 500mcm al in 4 inch conduit, rather than 2 parallel smaller feeds in separate conduit? I am trying to save $$ on wire, but if much better I will use cu. Trying to keep my voltage drop under 5%. Where I am at, voltage is usually about 122-124 to 244-248v. The underground section has 2x 90's and a large sweep that would equate to 90 degrees sweep.. I was a lineman many years ago so pulling wire shouldn't be that difficult.
Customer is a good friend of mine. I am just trying to be that good friend and Keep the cost down, but still give him a quality and smart installation.
We also have a 10kw pv system that will be tying into the line side of the meter main.
Your thoughts on the wire size/installation from the meter main to the 400 amp panel at the house are greatly appreciated.
Thank you.