How do you guys size branch circuits for residential ranges?
Do you use 220.19 and put anything under 12.5kw on a 40 amp, #8 circuit? OR do you size it at (100% or) 125% of the continuous load?
I don't like the 220.19 interpretation since it continually uses the terms "calculated" and "computed", referring to load calcs not branch circuit requirements.
This has become a contentious issue and need to resolve it.