hayeska
Member
- Location
- Rhode Island
Does the following Article and provisions apply to a resedential elecrical service.
The electrical panel is located in a 6 foot high basement; new construction.
Article 408 Switchboards, Switchgear and Panelboards
408.18 Clearances
(B) Clearances around switchboards and switchgear shall comply with the provisions of 110.26.
110.26(A)(4) Working Space About Electrical Equipment — Limited Access
(d) The space in front of the enclosure shall comply with the depth requirements of Table 110.26(A)(1). The maximum height of the working space shall be the height necessary to install the equipment in the limited space. A horizontal ceiling structural member or access panel shall be permitted in this space.
We would like to verify that such an installation meets the requirements of the code cited.
Thank you
The electrical panel is located in a 6 foot high basement; new construction.
Article 408 Switchboards, Switchgear and Panelboards
408.18 Clearances
(B) Clearances around switchboards and switchgear shall comply with the provisions of 110.26.
110.26(A)(4) Working Space About Electrical Equipment — Limited Access
(d) The space in front of the enclosure shall comply with the depth requirements of Table 110.26(A)(1). The maximum height of the working space shall be the height necessary to install the equipment in the limited space. A horizontal ceiling structural member or access panel shall be permitted in this space.
We would like to verify that such an installation meets the requirements of the code cited.
Thank you