Greetings,
When we size electrical service for a residential application, I use 220.82. Based on that the lighting and receptacles loads are factored at 40% when they are larger than 10 kVA.
But I do have also panel schedule spread sheets that consider lighting at 125% and receptacle at 100% of 90VA per each outlet.
During odd situations where we have so many receptacles in a property, then the feeder size gained from panel schedule spread sheets will be greater than what is gained from 220.82.
Now, the inspector is questioning me about that. He is saying that I need to size my feeder based on the spread sheet not based on the 220.82. Any recommendation how to respond?
Thank you in advance