Residential Feeder 83% rule .

Status
Not open for further replies.

Seekthetruth

Member
Location
Florida
Occupation
Electrical
310.15 B7 states that you can put 2/0(rated for 175 amps) on 200 amp breaker using the 83% rule. If your load calculation is 190 amps based on NEC 220 can 2/0 still be used or does NEC 215.2 A apply?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The load calculation gives you the OCPD size which is 200 amps. You take the 200 amps then apply the 83% rule and that is your minimum conductor size.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thanks for the input. It seems that NEC 215.2 A doesn't give that option
My response should have included the word feeder. A service or feeder supplying the entire load of a dwelling can use the 83% rule.


310.15(B)(7)(2)
For a feeder rated 100 through 400 amperes, the feeder conductors supplying the entire load associated with a one-family dwelling, or the feeder conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the feeder rating.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Remember that this only applies directly to services and feeders which supply the _entire_ load of a dwelling.
Well, it also applies to any other feeder of the same size on such a service, as there's no reason to use a larger wire for a subset of the load.

Cheers, Wayne
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Well, it also applies to any other feeder of the same size on such a service, as there's no reason to use a larger wire for a subset of the load.

Cheers, Wayne

Agreed. That is why I said 'directly'.

For example, consider a residence with a 200A service, with an outside meter main.

In the outside enclosure you have a 40A breaker for a heat pump, and a 200A feeder going into the house.

The 83% rule applies directly to the service conductors, but not to the 200A feeder going into the house.

But the 200A feeder doesn't need to be 'larger' than the service conductors. So _if_ you used the 83% rule to size the service conductors, then the 83% rule would come into play for the feeder.

However if you used full size service conductors then you couldn't later use the 83% rule for the feeder.

I forgot if as currently worded 'larger' means actual conductor size, or ampacity.

Jon
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician

For example, consider a residence with a 200A service, with an outside meter main.

In the outside enclosure you have a 40A breaker for a heat pump, and a 200A feeder going into the house.

The 83% rule applies directly to the service conductors, but not to the 200A feeder going into the house.

But the 200A feeder doesn't need to be 'larger' than the service conductors. So _if_ you used the 83% rule to size the service conductors, then the 83% rule would come into play for the feeder.

However if you used full size service conductors then you couldn't later use the 83% rule for the feeder.
As I read (2017) 310.15(B)(7)(3), you could.

Cheers, Wayne
I agree with Jon. If the SEC's are #3/0 Copper for 200 amps then you could not use #2/0 copper to size a 200 amp feeder.
 

frofro19

Senior Member
Location
VA.
Occupation
Master Electrician
The 83% rule applies directly to the service conductors, but not to the 200A feeder going into the house.
Is that because it's not serving the ENTIRE load of the house? I never understood that. If the heat pump Was included you could use the 83% rule but if you take some load away you can't. Makes no sense. I no you have the Ole diversity thing but if the conductors are adequate enough for everything they surly should be adequate for a lesser load.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I agree with Jon. If the SEC's are #3/0 Copper for 200 amps then you could not use #2/0 copper to size a 200 amp feeder.
I'm having trouble understanding how (2017) 310.15(B)(7)(3) could be read that way.

"(3) In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.15(B)(7)(1) or (2)."

So if (1) specifies that a 200A service need only have an ampacity of 166A, then any downstream feeder need only have an ampacity of 166A. You might choose to upsize some conductors above the minimum size and end up with a higher ampacity, e.g. for voltage drop, but that doesn't change that the maximum required ampacity is 166A.

Cheers, Wayne
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
I concur with Wayne's reading of the 2017 code. I believe an earlier version of the code went by service conductor size, however.

This allowance does not defeat the intent of the 83% rule, because in only applies in situations where the feeder rating is as large as the service rating.

In other words you can apply the 83% rule to a 200A feeder supplied by a 200A service, even if that feeder only carries part of the residential load. But you couldn't use the 83% rule to size a 100A feeder on a 200A service.

Think about it: if 166A service conductors are sufficient for a 200A rated service, why would they not be sufficient for 200A less the heat pump load?

Jon
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
I believe an earlier version of the code went by service conductor size, however.
Yes, the last version of the NEC without the 83% formulation was 2011, and the relevant sentence from 310.15(B)(7) there is "The feeder conductors
to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors." Which goes off the actual ampacity installed, rather than the minimum size allowed per Table 310.15(B)(7). Which was obviously a problematic formulation, leading to a variety of undesirable corner cases.

Cheers, Wayne
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I'm having trouble understanding how (2017) 310.15(B)(7)(3) could be read that way.

"(3) In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.15(B)(7)(1) or (2)."

So if (1) specifies that a 200A service need only have an ampacity of 166A, then any downstream feeder need only have an ampacity of 166A. You might choose to upsize some conductors above the minimum size and end up with a higher ampacity, e.g. for voltage drop, but that doesn't change that the maximum required ampacity is 166A.

Cheers, Wayne
You're correct. I was thinking of the pre-83% version like this from the 2008 which stated that "the feeder conductors
to a dwelling unit shall not be required to have an allowable ampacity rating greater than their service-entrance conductors."
 
Location
Seattle
Occupation
Electrician
I thought I watched a video here that said a feeder need not be larger than the service conductor. This being outside the 310.12(A) (B) where it is feeding the whole dwelling load.
I have a 400A service that terminates in a main panel. loads spit off in the main 400A panel. Then I have a set of 400A feed through lugs that will go to another 400Amp panel. Table 310.12 says I can use Copper 400 from the meter to the main service panel. Is there not an exception somewhere that says I don't have to make the wires from the main service panel to the subpanel larger than the service wires?
 