Residential Fire Pumps

Status
Not open for further replies.

John120/240

Senior Member
Location
Olathe, Kansas
Have you looked at NEC 695 ? For what few residential fire sprinkler systems that I have seen, they have always relied on adequate water pressure in the city pipe.
 

RICK NAPIER

Senior Member
Location
New Jersey
If your installing a pump for a NFPA 13D system which is for one and two family dwellings article 695 does not apply. NFPA 13D article 5.1.3 states that pumps do not need to be listed and 6.2(5) says a well pump is sufficient for this system. There may be some requirements from NFPA 13 but your installation will fall under the first four chapters of the NEC.
 
Last edited:

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
As Rick said, 13D systems are different. The purpose of 13D systems isn't to put out the fire, it's to extend the evacuation window so residents have a chance to beat feet in time.
 
Status
Not open for further replies.
Top