Trowbridge - Martin
New galvanized gas piping is installed for one new gas range in existing single family home. Florida Building Code Residential Fuel gas states:
CHAPTER 24 RESIDENTIAL FUEL GAS
G2411.1 (310.1) Gas pipe <<bonding>>. Each above-ground portion of a gas piping system that is likely to become energized shall be electrically continuous and <<bonded>> to an effective ground-fault current path. Gas piping shall be considered to be <<bonded>> where it is connected to appliances that are connected to the equipment grounding conductor of the circuit supplying that appliance.
It appears that no external bonding is necessary to the pipe from: service equip enclosure, the grounded conductor at the service, the grounding electrode conductor or to one or two of the grounding electrodes used.
Second question - if copper water piping is bonded at tank can outside water pipe ever be used for gas pipe bond?
Thank you, Tom
Thank you, Tom