HoosierSparky
Senior Plans Examiner, MEP
- Location
- Scottsdale AZ
- Occupation
- Senior Plans Examiner
Will generator emergency off switch act same as local disconnect switch you clouded?Is a lockable disconnect required between ATS and generator? Generator has an exterior toggle switch to turn off generator. The breaker is internal to the generator case.
View attachment 2559695
The toggle switch mounted on the generator does not meet the requirements off 445.18 .b. you must have a remote prime mover shutdown switch. It cant be in the generator enclosure or on the generator.OK, it seems a disconnect prior to the ATS is not required with the circuit breaker in the genset. The toggle on the exterior of the genset serves as a shutoff. Doesn't seem right, but it is what it is.......................................
Thanks all for your comments.
The disconnect might not be required but If it is greater than 15 KW a remote prime mover shutdown is.OK, it seems a disconnect prior to the ATS is not required with the circuit breaker in the genset. The toggle on the exterior of the genset serves as a shutoff. Doesn't seem right, but it is what it is.......................................
Thanks all for your comments.