jeramiepluemer
Senior Member
- Location
- Wisconsin
- Occupation
- Electrician
445.13 state I have to size generator 115% of name plate.
Propane
108.3x1.15=124.54 amps
Natural Gas
93.8x1.15= 107.87 amps
26kw 110 amp breaker in it.
Exceptions rule is what I don't under stand. Is is talking about the 110 amp breaker on gen. Customer has 200 amps panel. so for propane i use 2 copper and NG I use 1 awg aluminum.
Propane
108.3x1.15=124.54 amps
Natural Gas
93.8x1.15= 107.87 amps
26kw 110 amp breaker in it.
Exceptions rule is what I don't under stand. Is is talking about the 110 amp breaker on gen. Customer has 200 amps panel. so for propane i use 2 copper and NG I use 1 awg aluminum.