Mkopro97
- Boulder Colorado
I encountered a residence where the owner installed a new garage separate from the main house. They moved the overhead service from the main house to the garage. The overhead service comes into a meter housing then feeds the main disconnect inside the garage (via a 4? nipple). The main disconnect is grounded via a #6 grounding electrode conductor to a ground rod. From main disconnect (200A panel) there is a feeder that goes underground (to the main house via 4/0 AL underground feeders to a 200A external panel (no conduit). No ground wire run with the underground (direct burial) feeders. From the exterior panel on the house there is a 100A (SER) feeder to an old 100A pane inside the house. Along with the 100A feeder the installer ran a #4 bare copper wire alongside the 100A SER. The #4 copper wire is connected to the cold water supply in the house and the other end is connected to the 200A panel outside?s grounded (neutral) terminal. There is also a #4 CU ground wire from the cold water pipe to the old 100A panel. The 100A panel has a separate ground bar where the equipment grounding conductor from the SER and the #4 CU are connected. They are not connected to the neutral in this 100 panel. How should this mess be grounded? Thanks.