I am being told all residential home runs now must be in EMT or MC. Where are my associates getting this? Any ideas?
I am being told all residential home runs now must be in EMT or MC. Where are my associates getting this? Any ideas?
There is something in the '08 and/or '11 code that says if your homerun is in conduit you can use an AFCI device instead of a breaker.
210.12 Arc-Fault Circuit-Interrupter
Protection
(A) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall be
protected by a listed arc-fault circuit interrupter, combina-
tion-type, installed to provide protection of the branch cir-
cuit.
Exception No. 1: If RMC, IMC, EMT, Type MC, or steel ar-
mored Type AC cables meeting the requirements of 250.118
and metal outlet and junction boxes are installed for the
portion of the branch circuit between the branch-circuit
overcurrent device and the first outlet, it shall be permitted
to install an outlet branch-circuit type AFCI at the first out-
let to provide protection for the remaining portion of the
branch circuit.
Exception No. 2: Where a listed metal or nonmetallic con-
duit or tubing is encased in not less than 50 mm (2 in.) of
concrete for the portion of the branch circuit between the
branch-circuit overcurrent device and the first outlet, it shall
be permitted to install an outlet branch-circuit type AFCI at
the first outlet to provide protection for the remaining por-
tion of the branch circuit.
Exception No. 3: Where
Found it.
RMC IS the way to go..I can't find it either. My fellow electricians are by no means ignorant. I wonder where they got this? What about RMC or flex, for example? I am currently in central Alaska. I will check local codes tomorrow.
I am being told all residential home runs now must be in EMT or MC. Where are my associates getting this? Any ideas?