Just wanted to know if the inspectors in your area are enforcing 300 5 D 5 UF is a pain but required.
I know we've been through this before and I agree with you here.Some, like Charlie Trout, feel UF in an raceway is a violation.
I would go as far as to say the NEC allows cable assemblies such as NM or UF to be installed in conduit systems by the wording of 334.12(A)(1), this would imply NM could be run within a conduit, which in turn would allow UF per 340,10(4), then in chapter 9 "Notes to Tables" note 9 we are given the method to calculate these type cables for conduit fill.I don't really see an issue or problem.
To start with, I think "open runs" is a bad use of terminology and would be better stated as "exposed runs".Originally posted by roger:
Back to the reference of 334.12(A)(1) if NM is not allowed to be installed in a conduit (an enclosed run) why would the words"As open runs" need to be included?
"exposed runs" may not have been the intent, therefor the term was never considered.To start with, I think "open runs" is a bad use of terminology and would be better stated as "exposed runs".
You may be right, but what would the problem be with "open runs" above dropped ceilings? The only thing that I can think of is if the ceiling and/or panels were to be removed, you would then have "exposed runs" of NM that were before just "open runs". I believe there may be a code change for this for the 2005?Originally posted by roger:
Roger
Originally posted by bphgravity:
Yes, I wire homes in North Port, Sarasota just a few counties south of you I believe and we are required to use UF to islands and floor boxes.[/QUOTE)Bryan either you are or you aren`t using UF in a slab!!Yes we could use thhn and J boxes,but the time involved is a waste.We started a large custom Friday it has 2 1 " conduits slabbed.It has all the things I previously said plus an insta hot and a cook top.
Previous to this nm was not a problem but with 8-3 we now have a nightmare.