Residential load calc.

Status
Not open for further replies.

gregor

Member
Location
Cincinnati
I just started teaching exam prep for our apprenticeship.We are working on Resi. Service calcs.In annex D ex.D1(a) the calc only uses the dryer motor va at 100% .In D1 (b) the largest motor va is used +25% for a total of 125% and refers us to 430.24. Why didn't they do that in ex.D1(a)?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I also agree with Brad (just trying to boost your ego, buddy :lol: ). But I have a different reason. 220.54 gives us clear instructions of how to handle dryers. It says to use 5000 VA or the nameplate rating. It does not tell us to add 25% to either of those numbers.
 