I am currently involved in a brooha (battle) with an inspector in a small Florida town who will not accept my load calculations for a generator installation.
Here is the scenario:
He is insisting that 220.30(C)(6) does not apply. His contention is that
424.3(B) (2002 NEC) or 424.3(B) (2005 NEC) requires heating to be included at 125% in the load calculation because it is considered a continuous load and that 220.30(C)(6) is not a valid calculation.
I have tried to explain that this article only refers to branch circuit sizing but he will not buy into it.
His reply is to quote an NFPA opinion that says heat should always be figured at 125%.
Has anyone else ever heard this argument and if so, how did you deal with it?
In the end, I will probably end up shedding the heat load but I would like to make my stand and not have to go back to the customer for additional costs.
Here is the scenario:
He is insisting that 220.30(C)(6) does not apply. His contention is that
424.3(B) (2002 NEC) or 424.3(B) (2005 NEC) requires heating to be included at 125% in the load calculation because it is considered a continuous load and that 220.30(C)(6) is not a valid calculation.
I have tried to explain that this article only refers to branch circuit sizing but he will not buy into it.
His reply is to quote an NFPA opinion that says heat should always be figured at 125%.
Has anyone else ever heard this argument and if so, how did you deal with it?
In the end, I will probably end up shedding the heat load but I would like to make my stand and not have to go back to the customer for additional costs.