I am having a 3 ton heat pump replaced and was going to upsize the backup strips from 10kw to 15kw. The 10kw can't seem to keep up when the temps get down in the teens. Using Mike Holts load calculation form shows that the service to our house is already undersized. One question I have about the form. My outside unit shows the fan at 1 fla and the inside fan at 2.4 fla. I don't understand the large default numbers of 1600va in the fan/blower column. What am I missing?