Residential load calculation

Merry Christmas
Status
Not open for further replies.

nizak

Senior Member
Should the following items be considered part of the 3VA general lighting and general use receptacle outlet load?

- sump pump
- sewage ejector
- garage door openers
- central vac system

Also:

Is a detached outbuilding figured at the total VA of the breaker that's feeding it?



Where I'm located in Michigan, the POCO is no longer just "handing out" 320/400 A meter bases.
We have to show documented calcs justifying the load.

Many times unless there's a lot of in floor heat it's difficult to show a load that couldn't simply be served by a 200A service.

Thanks
 
No they should not be a part of the 3va

The load is figured on the actual load not the breaker feeding the building.
 