I'm doing a residential load calculation to show that a 30kw generator is sufficient to carry the total load.
Note: Service consists of (1) 320A meter can feeding (2) 150A Service rated automatic transfer switches.
3459 Sq ft, (2) Appliance, Laundry, 8kw range, 5kw dryer, 3kw water heater and A/C w/10kw heat.
I used 220.82 and ended up with 29kw and change after demand and with heat @100%.
County turned it down because 220.82 states that "This section applies to a dwelling unit having the total connected load served by a SINGLE 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors with an ampacity of 100 or greater."
In talking to one of the processors, their take is that since I have (2) separate mains feeding the house 220.82 does not apply.
My interpretation is that there is but one service to the dwelling, and that both feeders are fed from that single service and that the calculated load for the entire service is what both the incoming power and the generator will see.
Been in the trade awhile and have never had to ask how many mains a residence will have before doing a load calc.
Input?
Note: Service consists of (1) 320A meter can feeding (2) 150A Service rated automatic transfer switches.
3459 Sq ft, (2) Appliance, Laundry, 8kw range, 5kw dryer, 3kw water heater and A/C w/10kw heat.
I used 220.82 and ended up with 29kw and change after demand and with heat @100%.
County turned it down because 220.82 states that "This section applies to a dwelling unit having the total connected load served by a SINGLE 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors with an ampacity of 100 or greater."
In talking to one of the processors, their take is that since I have (2) separate mains feeding the house 220.82 does not apply.
My interpretation is that there is but one service to the dwelling, and that both feeders are fed from that single service and that the calculated load for the entire service is what both the incoming power and the generator will see.
Been in the trade awhile and have never had to ask how many mains a residence will have before doing a load calc.
Input?