Residential outlet spacing

Status
Not open for further replies.

gharris

Member
I remember that residental electrical outlets shall be installed along any useable wall space 2' or more; however, is the room spacing fpr receptacles12' oc? For some reason 6' oc sticks in my mind but that can't be.

[ June 03, 2003, 12:06 AM: Message edited by: gharris ]
 

stamcon

Senior Member
Re: Residential outlet spacing

No point of the wall along the floor shall be more than 6' from a receptacle. This means a receptacle needs to be located within 6' from a wall opening and then no more than 12' apart after the first one.
 
A

a.wayne3@verizon.net

Guest
Re: Residential outlet spacing

Yes it is 2` 6 ` and 12`,but you stated useable wall space here we are required to have a receptacle on any 2 ft wall in a room even behind a door
 

bphgravity

Senior Member
Location
Florida
Re: Residential outlet spacing

When designing the layout of todays typical home, one receptacle every twelve feet is hardly sufficient.

I believe this requirement was established to provide at least one receptacle outlet on each wall of a room and because manufacturers of cords on equipment were at 6 feet.

The overuse of extension cords and plug strips are leading causes of fire and electrical injury and damage within the home.

High use areas such as behind TV locations, next to beds, and computer equipment locations need addition receptacles above the requirements of the code.

Just my opinion. :)
 

ryan_618

Senior Member
Re: Residential outlet spacing

I agree with gravity. Also note that the 1999 NEC removed the word "usable" from 210.52

[ June 03, 2003, 01:02 PM: Message edited by: ryan_618 ]
 

michael nye

Member
Location
California
Re: Residential outlet spacing

every 12' of wall space is great but, what is a more practical application, is 2' inside the door, then when the I get to a corner I treat it as a new wall space and wire in another one. This accomidates most electrical apperaties 6' cord, and alliviates the need for extention cords .
 

bphgravity

Senior Member
Location
Florida
Re: Residential outlet spacing

I meet the requirements of the code as far as wall space goes, then I add for additional receptacle outlets in each corner if one does not end up there per code spacing. I then add quad receptacles to the nearest outlet next to any phone and cable outlet. This allows for multiple equipment us in these areas.

I make the use of quads a practice in kitchens as well. :)
 
Re: Residential outlet spacing

I think the key to any wiring job remember Nec is the minimum.I`d hate to wire a house with rec. spacing at minimum.Even for the tight wad contractor it only cost me a few bucks to be proud to have my name on the panel cover.

"by the work one knows the worker"
 

bennie

Esteemed Member
Re: Residential outlet spacing

If I build a house in the States where all of you gentlemen live, I know who to call for the wiring.

I am out of the trade now, but I know I won't be missed. Keep up the same attitude :D
 

racraft

Senior Member
Re: Residential outlet spacing

If you put a quad outlet in my house without my permission I might make you tear it out and replace. it with a duplex!

On all my electronic equipment (TVs, microwave, stereo, VCR, DVD, etc.) I use surge protectors. In some cases I like to use the six outlet type that plug directly into a duplex outlet with no cord. Your quad outlets make this a little difficult.

My computers are on UPS devices, so they don't require more than a single outlet either.
 

bphgravity

Senior Member
Location
Florida
Re: Residential outlet spacing

Originally posted by racraft:

On all my electronic equipment (TVs, microwave, stereo, VCR, DVD, etc.) I use surge protectors. In some cases I like to use the six outlet type that plug directly into a duplex outlet with no cord. Your quad outlets make this a little difficult.
These are horrible devices that should be banned from being manufactured. If there is ever the over use of a single receptacle outlet, it is with use of these type of devices. I would rather see a six-strip, surge protected, cord-and-plug connected device, but I dont like these either. Just my opinion.
;)
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: Residential outlet spacing

I place the outlets where they make the most sense. Then I touch the wall and spread my arms. If an outlet is within my reach I know that I am ok. Your arm span is your height.

Saves getting the tape out all the time. It is also an easy way to show the homeowners, during a walk-through, what is going on. They can see your arms spread. They cannot see your tapes reading.

Mike P.

[ June 04, 2003, 08:09 AM: Message edited by: jxofaltrds ]
 

gharris

Member
Re: Residential outlet spacing

Thanks so much for all of your responses. I knew 6' was in there somewhere. I haven't inspected homes in almost 20 years and I couldn't find my latest NEC. I lived in CA for years and now am in the DC area. We are building a new home and I don't know where these inspectors got their training. It's awful the things that go on back here, and the shoddy way things are done around here is a disgrace to the inspection profession. I'm lucky if we have one outlet on each wall of our new home. And, our rooms are huge. I checked and the jurisdiction where our home is being constructed and they use the NEC. And, before I made a fuss I wanted to be sure. I'll go to the library and look up the code section and then make a fuss!! Most times men don't like to hear this type of stuff from a woman. Thanks for the info. :) )
 