Residential overhead Panel/Meters

Status
Not open for further replies.

Gregorio

Member
Location
Hesperia Ca USA
HI, next week (Mon) we're installing a typicall 100 to 200amp panel upgrade and I cant find a Table to verify it
is ok to install 2/0 in our weather head pipe (11/2") or must we use 3/0?
 
2014 NEC has made a change-- 310.15(B)(7)(2). 2/0 copper is fine for a residence

What change? 2/0 copper/ 4/0 alm has been ok for 200 amps for res for the 45 years I've have been working. Check with local POCO. They usually has say so over riser requirements. FPL has a 2" riser requirement if used for support.
 